NEC Sections 210.23(A) through (E)

12 replies·135 views
1 month ago#611187(edited 1 month ago)
NEC Sections 210.23(A) through (E), of the 2023 edition of the NFPA 70, text sourced from https://up.codes/
210.23 Permissible Loads, Multiple-Outlet Branch Circuits
In no case shall the load exceed the branch-circuit ampere rating. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size in accordance with 210.23(A) through (E) and as summarized in 210.24.
210.23(A) 10-Ampere Branch Circuits
A 10-ampere branch circuit shall comply with the requirements of 210.23(A)(1) and (A)(2).
210.23(A)(1) Loads Permitted for 10-Ampere Branch Circuits
A 10-ampere branch circuit shall be permitted to supply one or more of the following:
1. Lighting outlets,
2. Dwelling unit exhaust fans on bathroom or laundry room lighting circuits,
3. A gas fireplace unit supplied by an individual branch circuit
210.23(A)(2) Loads Not Permitted for 10-Ampere Branch Circuits
A 10-ampere branch circuit shall not supply any of the following:
1. Receptacle outlets
2. Fixed appliances, except as permitted for individual branch circuits
4. Garage door openers
5. Laundry equipment
210.23(B) 15- And 20-Ampere Branch Circuits
A 15- or 20-ampere branch circuit shall be permitted to supply lighting outlets, lighting units, or other utilization equipment, or any combination of them, and shall comply with 210.23(B)(1) and (B)(2).
Exception: The small-appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (C)(2), and (C)(3) shall supply only the receptacle outlets specified in that section.
210.23(B)(1) Cord-and-Plug-Connected Equipment Not Fastened in Place
The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
210.23(B)(2) Utilization Equipment Fastened in Place
The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
210.23(C) 30-Ampere Branch Circuits
A 30-ampere branch circuit shall be permitted to supply fixed lighting units with heavy-duty lampholders in other than a dwelling unit(s) or utilization equipment in any occupancy. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
210.23(D) 40- And 50-Ampere Branch Circuits
A 40- or 50-ampere branch circuit shall be permitted to supply cooking appliances that are fastened in place in any occupancy. In other than dwelling units, such circuits shall be permitted to supply fixed lighting units with heavy-duty lampholders, infrared heating units, or other utilization equipment.
210.23(E) Branch Circuits Larger Than 50 Amperes
Branch circuits larger than 50 amperes shall supply only nonlighting outlet loads.
1 month ago#611188
Post #135080
1 month ago#611269
The Scenario: You locate a 20-Amp circuit breaker in a house basement. It's wires lead to the first floor and has has two outlets. One outlet has a fixed-in-place 12-Amp dishwasher.
Based on your knowledge of 210.23, is this a violation? (Hint: Look back at the 50% rule in 210.23(A)(2))
1 month ago#611270
Post #135080
User avatar
777

india was aryan first

1 month ago#611331
what is this
1 month ago#633735
We all do this
User avatar
DoomKillerPL

A Foxgirl With Lots of Validation 🦊🏳️‍⚧️🇵🇱

1 month ago#634316
Post #213488
1 month ago#634364
DoomKillerPL
Post #213488
Everyone who doesn't want a circuit overload with their ovens, outlets and have them work cares about this
1 month ago#634373
SECA
User avatar
melissa

🏳️‍⚧️Trans🌸 | 🏳️‍⚧️She/Her!!🏳️‍🌈 | Lesbian🏳️‍🌈 | 🐈Furry🦊 | 🇺🇦🇹🇼🇮🇱 | Autistic🧩 |DNI🔞

1 month ago#634379
im sorry that happened or happy for you idk im not reading this
1 month ago#634381
>Words, science, robots, blah blah blah
1 month ago#634420
>Words, science, robots, blah blah blah
Post #142196
>even doe this is literally just the legal requirements to install an outlet and a microwave on the same circuit without it exploding
1 month ago#634446
melissa
im sorry that happened or happy for you idk im not reading this
Massa I can't be readin' dis izza too hard mane
Log in to reply to this thread.